I'm with mnementh on that one - I still think a properly made up wire-nutted connection is better than those little spring things. Not as fast or easy to make up, but there's much greater contact area than you get with the spring terminals, and it makes a good solid connection if the wires are properly twisted with a pair of pliers before the wire nut is installed.
-Pat
I believe we have instruments that can test electrical properties.
This is "FK" cable, 7-strand 1,5mm
2 (around AWG15), two pieces per sample joint of about 18cm per piece. The stripping was done to manufacturers requirement, 11mm for 221 clamp, and 15mm for Torix
(tm). Wires were pre-twisted in the nut. This is not required, especially not if you are using a 1/4" bit holder in a Makita or similar to twist the Torix -- that is explicitly allowed and recommended by Schneider who make them. I hand-twisted here, and then it is easier to do a bit of pre-forming by hand.
It is, in practice, a tie. At 100Hz, there was no difference. At 1KHz, the 221 wins by 3mΩ.
I will push 10A through them and test voltage drop. That's probably going to weed the differences out.