Author Topic: Jaycar Powertech 1500va UPS circuit/schematic  (Read 2578 times)

0 Members and 1 Guest are viewing this topic.

Offline paulnTopic starter

  • Contributor
  • Posts: 28
  • Country: au
Jaycar Powertech 1500va UPS circuit/schematic
« on: March 05, 2013, 01:14:00 am »
During a recent power outage my UPS failed to work!!  Anyway checking the batteries showed they we U/S.  Replaced and all seemed OK i.e. they charged up OK.  On test with a load connected the unit switches over OK - but shows no load % used, then shuts down after a couple on minutes.  The manual mentions if the UPS "appears to see no load" it will turn it self off after a minute or 2.  The unit appears to work otherwise i.e. the capacity decrements as expected.  So I guess if there is some way to turn off the "no load" option it would be a cheap fix, otherwise looking for ideas or circuit.
Thank You
 

Offline PeterG

  • Frequent Contributor
  • **
  • Posts: 835
  • Country: au
Re: Jaycar Powertech 1500va UPS circuit/schematic
« Reply #1 on: March 05, 2013, 02:08:42 am »
If you contact Jaycar they will most likely provide you with the schematic.

Regards
Testing one two three...
 

Offline paulnTopic starter

  • Contributor
  • Posts: 28
  • Country: au
Re: Jaycar Powertech 1500va UPS circuit/schematic
« Reply #2 on: March 05, 2013, 02:27:05 am »
If you contact Jaycar they will most likely provide you with the schematic.

Regards

Already tried phone and email to Jaycar - and a personal request to local store - with out success.  Hence my post.
 