Attention because simply switching off the mains AC power supply of the UPS is not representative of what is actually happening and the results may not be the same as those that occur during a power outage.
Indeed, the lack of AC voltage is often the result of a fault located upstream, far from the UPS .... the entire distribution network then appears as a short circuit and not an open circuit.
This may cause the UPS to operate quite differently during load transfer.
The transfer test must be done in a different way: the UPS is protected by a low-intensity external fuse and the AC input is short-circuited by a contactor.
The fuse blows and the AC input of the UPS feels a short circuit.