Dig by each one to find the cabling, and see how they are wired. If all 4 are wired in a chain then look at the cable leading to the house and follow the line, you will generally find that electricians go point to point.
Armoured cable can be the stuff referred to above, or even older is steel tape armoured cable, which originally had a lead inner sheath, a bitumen coat and 2 wound steel tapes on the outside, all originally covered with hessian cloth impregnated with bitumen. After a century underground you find the bitumen is gone, but the cable otherwise is in good order, even in the ground near the sea. Still hundreds of kilometers of it in use here, at various voltages from 230VAC to 66kV, all direct buried. Was fun one day when a building site 300m away was digging with an excavator and picked up the 11kV feeder for us, as he pulled it up one phase dropped, then the second then the cable finally tripped out on the substation breaker. Took 3 hours to isolate the segment and get power back to the local grid.