How does a grid fed inverter check if it needs to shut of power to the grid if, for example the grid is down due to work or maintenance?

Does it stop producing and Poll for a voltage every x ms or does it use something cleverer (<-And is that even a word?)?
 

Offline bilko

  • Frequent Contributor
  • **
  • Posts: 405
  • Country: 00
Re: Grid Fed Inverter Electrocuting lines men?
« Reply #1 on: July 04, 2013, 11:38:59 pm »
A grid tie inverter has to synchronise its output to the AC on the grid else the grid will send the smoke out of the inverter.   ;)
 

Offline IanB

  • Super Contributor
  • ***
  • Posts: 12424
  • Country: us
Re: Grid Fed Inverter Electrocuting lines men?
« Reply #2 on: July 04, 2013, 11:43:28 pm »
Also if you are wise and you want to ensure your safety, you will place a short (a "crowbar") across the circuit you are working on after you have de-energized it and checked for no voltage. Then if anyone or anything tries to energize the circuit without permission it will trip the overload cutout.
 

Offline johnnyfpTopic starter

  • Frequent Contributor
  • **
  • Posts: 261
  • Country: nz
Re: Grid Fed Inverter Electrocuting lines men?
« Reply #3 on: July 04, 2013, 11:50:51 pm »
Makes sense.

How often does it sync up with the mains? (I know it's dependent on the model but they should all be similar, in the sense is it ever milliseconds or every minutes?).
 

Offline dr.diesel

  • Super Contributor
  • ***
  • Posts: 2214
  • Country: us
  • Cramming the magic smoke back in...
Re: Grid Fed Inverter Electrocuting lines men?
« Reply #4 on: July 04, 2013, 11:55:46 pm »
At least for Duke Energy, the largest utility in the States, you are in no danger with a grid tie inverter or generator.  All line work is done with all 3 phases shorted with heavy gauge wire.  Also remember, anything attempting to backfeed would also be feeding whatever portion of the grid it's still connected to, likely a huge load.

Offline gxti

  • Frequent Contributor
  • **
  • Posts: 507
  • Country: us
 

Offline johnnyfpTopic starter

  • Frequent Contributor
  • **
  • Posts: 261
  • Country: nz
Re: Grid Fed Inverter Electrocuting lines men?
« Reply #6 on: July 05, 2013, 12:09:05 am »
Thanks! I didn't know it was called Islanding, but useful bit of information.

 

Offline bilko

  • Frequent Contributor
  • **
  • Posts: 405
  • Country: 00
Re: Grid Fed Inverter Electrocuting lines men?
« Reply #7 on: July 05, 2013, 09:17:17 am »
Makes sense.

How often does it sync up with the mains? (I know it's dependent on the model but they should all be similar, in the sense is it ever milliseconds or every minutes?).
Not sure, I would say at least every cycle.
 

Offline G7PSK

  • Super Contributor
  • ***
  • Posts: 3865
  • Country: gb
  • It is hot until proved not.
Re: Grid Fed Inverter Electrocuting lines men?
« Reply #8 on: July 05, 2013, 03:13:58 pm »
I would also expect that after the grid has gone down any inverter on line would see the grid load as a short and shut down or burn up, most people will just leave everything on that was on went the power failed.
 

Offline Jeroen3

  • Super Contributor
  • ***
  • Posts: 4198
  • Country: nl
  • Embedded Engineer
    • jeroen3.nl
Re: Grid Fed Inverter Electrocuting lines men?
« Reply #9 on: July 05, 2013, 10:31:55 pm »
If there is no grid, there is nothing to sync to.
You probably need to manually restart it, after opening your grid circuit breaker. (you don't want to power the neighbors do you?)

It must make sure there is synchronisation. If it loses that, energy might want to go back in the inverter.
« Last Edit: July 05, 2013, 10:35:19 pm by Jeroen3 »
 