Siwastaja, I don't disagree with you regarding the Twente study. However it served its purpose it highlighted the problem and other teams looked at the issue too.
Yes I can, and I did with my central heating pumps. The datasheet for the pump has a chart that shows power consumption at each setting (there are 6 settings, 3 constant pressure, and 3 constant flow). I set the pumps to the lowest setting. I switched off all the circuits in the breaker panel other than the pumps overnight and I took readings before I went to bed. Then in the morning. Instead of few tens of watts the load registered was close to 200W.
OK, this is indeed interesting.
1) You are 100% sure there are no other loads? Did you let your refrigerator and freezer warm up during night? Can you repeat the same with the circulation pump turned off as well, to verify zero reading? And I mean, turned off at the pump, not at the breaker - sometimes house wiring contains surprises like undocumented branches.
I'm as sure as one can be. I guess 99%?. My fridge/freezer is fine without electricity if it isn't opened for 7h or so. It is a new build house I was involved with building every step of the way. I didn't watch the electrician put in the wiring, but I have the schematic. I will be 100% sure when I have the CTs arrive and I measure the waveform right in front of the meter and compare with the readings.
2) What does it mean to have "load registered to 200W"? Is this load number reported by the meter in Watts? Or did you calculate it by (morning_kwh - evening_kwh) / hours_between_readings? The latter should give you the correct result.
I compared the readings before I went to bed, and then first thing in the morning (I even took pictures back then). It shows usage to 1/10th of a kWh.
Also with this meter it is possible to "read" current usage by measuring the time between the "ticks". It blinks the led every so many watt-hours. I can't currently remember how often (this was over a year ago). I spent lots of time doing that, switching off/on various citcuits, remeasuring etc.
Okay so re: some notes for that second longer paper (Contemporary electric energy meters testing under simulated nonsinusoidal field conditions)
The results presented in [17] suggest that digital meters are less subject to measurement errors as long as the signals are still compatible with the sampling process. However, the induction-type electricity metering devices are highly sensitive to the distortions in the supply voltage.
I can totally believe the above, in fact, I don't see how modern digital meters can be any less accurate than the old ones, in general (especially with nonlinear loads).
And:
Two meters
(in a total of six devices) presented errors greater than their respective accuracy classes. However, given that under nonsinusoidal conditions the MUTs’ error margins can be extended (according to the standards, as shown in Sect. 4.1), only one sample demonstrated the errors, which exceed its tolerance limits. All the deviations from the readings of the reference device were positive, the meters over registered.
The absolute worst error above was ~+8%, when the vast majority of meters was much less than that. The Class 2 meters are allowed up to 6% error in those conditions, so TBH it's not too far off, and not worth losing your sleep over that extra 2%.
Other random points I gathered were:
- They injected 10kHz current waveform as a load. This is well beyond the BW of any 60Hz meter, so
- The quoted >60% error was for reactive power, not real power. Residential users don't get billed for reactive power. Moreover, in certain condition, you cannot calculate reactive power accurately when using CTs for current measurement. This is a fundamental math problem (CTs can't measure even harmonic currents), not a accuracy/resolution/whatever problem.
All in all, that second paper, which is substantially more thorough and believable, would lead us to believe that this is a non-issue, even with special "engineered" waveforms designed to defeat the meters. They still use a "meh" reference meter, but it is a massive step-up from a mechanical one.
The point is not that modern meters are less precise than old ones, but that with high use of non linear loads creating choppy wavorms there is a significant error. You mentioned the highest error was 8% while 6% is allowable. Firstly, I didn't realise 6% error is allowable. If it is, that is less than ideal.
However, the purpose of the study wasn't to quantify actual error possible in real life with realloads. The goal in my opinion was to show that with non sinusoidal waveforms the meters show not insignificant errors.
Now another team should measure waveform that happen with actual use of dozens of LEDs and lots of other "modern" loads. Then see how meters fare with those waveforms.
Regarding your critique that injecting non sinusoidal waveforms with 10kHz frequencies into the ac line is unfair to a smart meter than usually handles 60Hz (50Hz here). In my opinion it is not a matter of fairness, but wmthe studies are bringing us closer to understanding if we are being charged correctly for our usage and generation. I can think of many loads that generate harmonics in tens of KHz in current as well as voltage (not at the same time of course, it is usually one or the other depending on what kind of load is it).
Also If my meter had an error of 8% (overcharging on usage and again under measuring on PV generation) I could loose 16% total if my PVs cover 100% of my usage. That in monetary terms is enough to think about what one can do to fix that on one's end.
I only use the 8% as an example. Currently what the true error is, is anyone's guess.
I think, as the cost of electricity becomes even more bonkers considerations like this will become more and more popular. Perhaps I should ping this thread in 2 years time. I bet there will be more interest in filtering etc. Perhaps there will be more research by then. Also, as time goes by more and more people will have houses that contain only non linear loads that try to limit their power use by pulling power in very short time steps (possibly at or even below the current detection limit). Then they will get readings that make no sense.
This is just an anecdote, but imagine my surprise when there were 2 months during which I had to use an electric resistive heater. I set up a simple power measuring device (plug with WiFi) not to be surprised by the bill. I used up around 30% more electricity during those two months. Then once the bill arrived I paid
less than usual for the time period(my bills are bi-monthly) Not by much, just few percent, but still this was bonkers. (The readings are not estimated, a guy from the electric company comes every month and physically reads the meter). Also I work from home, my usage is very consistent and predictable beyond the expected seasonal changes.
I'm mentioning the above not as proof, but just to demonstrate the kind of inconsistencies that do happen.