I wasn't sure if this should go into the renewables section, but I guess it applies to inverters in general so I posted it here.
I have a modern grid-tie transformerless PV inverter in H5 configuration. In Europe almost all budget inverters that meet the current regulatory requirements do not provide isolation between the PV side and the grid. Those inverters, when they operate put significant negative and positive voltages on the PV input. This is mostly fine, but my PV panels require the negative electrode to be at zero to ground or positive (reasons below). I've managed to find a low frequency medical isolation transformer at proper wattage to be able to isolate the inverter on the grid side and ground the PV-(minus) terminal hopefully.
However, before I risk my expensive(to me) inverter I decided to simulate everything in LTSpice and I discovered a potential issue I hope that perhaps someone could help me with(there are more issues, for example the inverter software measuring the grounding etc, I'm not worried about it at this stage - yet).
So below we have a simplified model of the inverter made up in LT-Spice(click to zoom in):
The isolation transformer can be disregarded in this schematic as AC neutral is tied to ground via 10 ohms here.
And here I show the waveforms present on the PV and AC output in normal operation. (click to zoom in)
You can hopefully see on the waveforms how the PV-(minus) terminal potential frequently reaches -600V. This is what I have to avoid.
So below we have a schematic of the same, but with isolation transformer "engaged" and PV- grounded.(click to zoom in)
And the respective waveforms. I added the red trace showing the differential voltage between AC live and "neutral" for clarity.(click to zoom in)
As you can see the goal for the PV-(minus) has been reached making it zero (or close to it) to ground. The differential AC voltage is still a nice sinusoid so the isolation transformer should make great use of it. However, the potential between AC (both live and neutral) and ground now contains very high frequency switching "stuff" and I'm not sure if this is not going to cause problems with my inverter. Does anyone have any advice how should I go about checking if this may be a problem? I can't open the inverter up due to warranty sticker, but I can probe various things from the outside. I have measuring equipment, rf generators, oscilloscopes etc available. I was thinking about starting with overcurrent protection inline with the PV and the isolation transformer in place, but putting low inductance potentiometers in both grounding paths(the AC neutral to ground and PV- to ground). Start with the AC side grounded and slowly shift to PV- side grounding hopefully catching any possible problems when they occur before they manage to blow up any parts. Any comments, suggestions?
The below is an explanation why I need this and alternative approaches It is relevant to this discussion only for context. I include it for information sake, but I would like to focus the discussion on the above.
So, why do my PV panels need it? Because they are thin film CIGS panels I bought for next to nothing at bankruptcy auction. They are made by a German company that went out of business because their panels suffer horrible potential induced degradation making them almost useless within few years if the minus terminal is at negative to ground potential for too long. Did I knew about it when I bought them?Yes, but I thought it is an opportunity to experiment. At worst I'll loose some time on my "hobby", at best I'll have a functioning PV system at 20% of the normal cost.
An alternative method to prevent PID is to glue conductive backing foil on the back of panels tied to each panel's PV- electrode therefore shifting "the ground" potential. The cause of PID is an electrostatic field in the soda lime glass used for the panel backing. The amount of PID(potential induced degradation) is directly proportional to the charge transferred by sodium ions in glass. If we can zero the field by making the back of the glass be at the same potential as PV- the problem is solved, ions become stationary again. I even bought enough one side conductive mylar foil to go down this route and it was my preferred one, but then I managed to get that isolation transformer for next to nothing. The inconvenience of having to glue that foil onto each panel, connect it reliably etc, set in and I decided to at least try the LF isolation transformer approach.
Hopefully this thread helps me in getting to the bottom of if I can use that isolation transformer and save myself the experience of gluing 30 sq. meters of mylar onto glass :-)