Author Topic: Is there a standard for Bus-Bar current rating calculation (copper)  (Read 762 times)

0 Members and 1 Guest are viewing this topic.

Offline aju11Topic starter

  • Contributor
  • Posts: 31
  • Country: in

 |O

Google search gives  ->  Current =1.2 x cross section

Is there any standard to prove this?

what are the considerations like length, thermal parameters while using factor 1.2?
 

Offline aju11Topic starter

  • Contributor
  • Posts: 31
  • Country: in
Re: Is there a standard for Bus-Bar current rating calculation (copper)
« Reply #1 on: February 18, 2022, 01:01:03 pm »
 Also, current capacity of wire is calculated by thumb rule:  Current = 4 x cross section Or sometimes 6 x cross section.

Why factor of 4 or 6 for wire? and Why factor of 1.2 for Bus bar.
 

Offline strawberry

  • Super Contributor
  • ***
  • !
  • Posts: 1199
  • Country: lv
Re: Is there a standard for Bus-Bar current rating calculation (copper)
« Reply #2 on: February 18, 2022, 01:06:00 pm »
acceptable power loss. ohms law
1mm^2 1m = 10W loss , 1mm^2 10m = 100W loss
 

Offline Berni

  • Super Contributor
  • ***
  • Posts: 5012
  • Country: si
Re: Is there a standard for Bus-Bar current rating calculation (copper)
« Reply #3 on: February 18, 2022, 01:07:12 pm »
It's not as simple as multiplying with a magic number. You want to use a table like this:
https://www.australwright.com.au/technical-data/advice/copper-busbar-rating/

For example a wide thin bus bar is going to have more cooling than a square crosssection and so be able to handle more current.

This is also the reason that wires can handle more current per crosssection area. The circumference of a wire does not change linearly with the crosssectional area. So this esentialy means a thin wire has more cooling capability per given crosssection and so can carry more current density
 

Offline strawberry

  • Super Contributor
  • ***
  • !
  • Posts: 1199
  • Country: lv
Re: Is there a standard for Bus-Bar current rating calculation (copper)
« Reply #4 on: February 18, 2022, 06:51:01 pm »
For example a wide thin bus bar is going to have more cooling than a square crosssection and so be able to handle more current.

if vertical but horizontal could be worse than square
cooling affected by surface area and airflow
shouldn't be much difference in cooling effect between wire size if conductor temperature is less than ~50C or minimal difference between conductor and ambient temperature
 