Author Topic: Different motor control modes  (Read 2244 times)

0 Members and 1 Guest are viewing this topic.

Offline BillTopic starter

  • Newbie
  • Posts: 8
  • Country: ch
Different motor control modes
« on: June 25, 2024, 02:04:13 pm »
Hello everyone,

I would like to know the different types of communication between an electric motor and a Siemens 1200 PLC. Although this depends on the type of motor used, I am particularly interested in the different connection modes. Are there (specific interfaces or connectors, relay) between these two systems?

Thanks
 

Offline Doctorandus_P

  • Super Contributor
  • ***
  • Posts: 3750
  • Country: nl
Re: Different motor control modes
« Reply #1 on: June 26, 2024, 11:23:00 am »
PLC's only do low power signals. So the interfaces would be something like a contactor, Frequency inverter, BLDC / Servo motor controller etc. Communication protocols can be anything from a few logic signals (contactor on) or to direct to inputs of the controller (on/off, forward/reverse) to any of the common industrial buses. (Modbus, EtherCAT, 4-20mA, HART etc).
 

Offline BeBuLamar

  • Super Contributor
  • ***
  • Posts: 1310
  • Country: us
Re: Different motor control modes
« Reply #2 on: July 09, 2024, 08:28:33 pm »
Often the PLC doesn't communicate with the motor directly. Generally the PLC would communicate with a motor drive either AC inverter or DC drive. The communication can be Profibus, Modbus RTU in the old days or today Profinet, Modbus TCP/IP, Ethernet IP, Ethercat, Powerlink etc... these use an ethernet connection.
 