Author Topic: The BIG EEVblog Server Fire  (Read 22458 times)

0 Members and 2 Guests are viewing this topic.

Offline madires

  • Super Contributor
  • ***
  • Posts: 8089
  • Country: de
  • A qualified hobbyist ;)
Re: The BIG EEVblog Server Fire
« Reply #50 on: April 08, 2021, 10:52:16 am »
I thought datacenters typically used Halon fire suppression systems? The last place I worked that had an onsite datacenter had one, there were warning strobes to indicate the system had discharged and asphyxiation warning signs.

Halon was banned, but old fire suppression systems may still use it. And there are a few alternatives, i.e. FM-200. Anyhow, you'll also find classic water based fire suppression systems in many data centers. Some of them create a misty spray.
 

Offline YurkshireLad

  • Frequent Contributor
  • **
  • Posts: 365
  • Country: ca
Re: The BIG EEVblog Server Fire
« Reply #51 on: April 08, 2021, 11:38:03 am »
My question is, are you staying with them or moving to another service provider?  :)
 

Offline Gyro

  • Super Contributor
  • ***
  • Posts: 9880
  • Country: gb
Re: The BIG EEVblog Server Fire
« Reply #52 on: April 08, 2021, 11:50:50 am »
My question is, are you staying with them or moving to another service provider?  :)

That's a question of whether you stick with the provider that's already had the fire, and hopefully learned something from the experience - or go with a new provider that hasn't had a fire yet;)
Best Regards, Chris
 
The following users thanked this post: SeanB, Damianos

Offline coppice

  • Super Contributor
  • ***
  • Posts: 9276
  • Country: gb
Re: The BIG EEVblog Server Fire
« Reply #53 on: April 08, 2021, 11:55:01 am »
Halon was banned, but old fire suppression systems may still use it. And there are a few alternatives, i.e. FM-200. Anyhow, you'll also find classic water based fire suppression systems in many data centers. Some of them create a misty spray.
In the early 80s the company I worked for kept changing its insurers each year. These alternated between pro-halon insurers and pro-water insurers. We had halon and sprinkler systems alternately installed and ripped out of the computer room I oversaw for several years.
 

Offline coppice

  • Super Contributor
  • ***
  • Posts: 9276
  • Country: gb
Re: The BIG EEVblog Server Fire
« Reply #54 on: April 08, 2021, 11:56:28 am »
My question is, are you staying with them or moving to another service provider?  :)
Why abandon one of the hottest operations in the business? Are you concerned their service may be cooling off now?
 

Offline YurkshireLad

  • Frequent Contributor
  • **
  • Posts: 365
  • Country: ca
Re: The BIG EEVblog Server Fire
« Reply #55 on: April 08, 2021, 11:56:47 am »
My question is, are you staying with them or moving to another service provider?  :)

That's a question of whether you stick with the provider that's already had the fire, and hopefully learned something from the experience - or go with a new provider that hasn't had a fire yet;)

True, or do you stick with a provider that had a fire or move to one that hasn't.  ;D

It is a business after all.
 

Online Ian.M

  • Super Contributor
  • ***
  • Posts: 13026
Re: The BIG EEVblog Server Fire
« Reply #56 on: April 08, 2021, 12:04:37 pm »
My question is, are you staying with them or moving to another service provider?  :)
Better the devil you know.   At least you can be fairly certain they'll put measures in place to prevent or reduce the impact of similar future incidents, and have some idea of their actual disaster recovery capabilities.

It would be nice if WebNX added a large NAS with its own power management in a shipping container at both their locations, with high bandwidth connectivity into their data centers.   Its only a bit over 600 miles as the crow flies between their locations, (729 miles by road, est. 10.5H driving time), so if they had another extended outage, the whole NAS could be shipped to their other location to facilitate getting fall-back servers online without the bandwidth implications of either uploading from off-site backups, or live syncing over a significant geographical distance.  They'd also need a priority standby contract with a local shipping company at each end to provide a self-loading container truck and two drivers with N hours notice 24/7.
« Last Edit: April 08, 2021, 12:14:02 pm by Ian.M »
 

Offline wilfred

  • Super Contributor
  • ***
  • Posts: 1253
  • Country: au
Re: The BIG EEVblog Server Fire
« Reply #57 on: April 08, 2021, 12:10:25 pm »
For prosperity....including the bad spelling:
Also for posterity.
 
The following users thanked this post: Microdoser

Offline wilfred

  • Super Contributor
  • ***
  • Posts: 1253
  • Country: au
Re: The BIG EEVblog Server Fire
« Reply #58 on: April 08, 2021, 12:21:56 pm »
My question is, are you staying with them or moving to another service provider?  :)

That's a question of whether you stick with the provider that's already had the fire, and hopefully learned something from the experience - or go with a new provider that hasn't had a fire yet;)

True, or do you stick with a provider that had a fire or move to one that hasn't.  ;D

It is a business after all.

The real question is were they prepared as they claimed they would be and did they recover as they promised they would. They can only control how they plan and respond. No-one knows which disaster scenario will play out. It could have been a Texas like power outage and the trucks delivering diesel for the generators may not have been able to get through to resupply.

I do think Dave could (should?) make preparations to restart from offsite backups. From what I read there was only 10% of servers water affected. How long would it have taken to recover from a total loss of all the site. I can't imagine sufficient servers would be readily available.

 

Offline cdev

  • Super Contributor
  • ***
  • !
  • Posts: 7350
  • Country: 00
Re: The BIG EEVblog Server Fire
« Reply #59 on: April 08, 2021, 12:44:14 pm »
They put their backup server in LA?

The city thats been cinematically annihilated more times than any other!

 Why one only needs to look at maps from not so long ago to realize that California is likely to tear itself off of the mainand and strike out on its own at it's earliest opportunity..

I figured this event needed it's own thread, so moved it from the servere reports thread.
HUGE thanks to gnif for handling this:
https://hostfission.com/


Fission? Degraded state?

The server was down from 2021-04-04 21:13 UTC to 2021-04-08 03:36 UTC

It's currently still operating in a degraded state, and performance is surrently impacted until the caches catch up.
Gorillaservers upgraded the server box (maybe the old box was water damaged?) from Dual Xeon 2620V2 from the older dual L5630

Presumably they'll upgrade the other redundant box too to match, but the 2nd box is not currently online yet.

The lesson here is, whilst it's great to have a fully redundant automatic backup server, it was kinda silly to have it in the same datacenter!
We are going to ask Gorillaservers is they can provision one of the boxes in their LA data center, so if a whole city/state goes out the server will still operate.


The city of LA is not a secure location. It's as insecure a location as there is in this country.

They suppress all news to the contrary, as a favor to the real estate industry.
Ive been told by a relative who was in a position to know.

They have lots of tornadoes (and waterspouts, of salty water, which Ive seen between the city and Santa Cataline Island. )
And substantial numbers of earthquakes.

I aslo learned the importance of relying on a single email server. I was surprised at the stuff I couldn't do that relied on my primary email for confirmations etc.
[/quote]

Its truly horrible how much we depend on easily broken computers and unreliable networks.

What if (insert unspeakable tragedy here) ? Huh?

what if.. We need more resilience and redundancy..
« Last Edit: April 08, 2021, 12:52:48 pm by cdev »
"What the large print giveth, the small print taketh away."
 

Offline madires

  • Super Contributor
  • ***
  • Posts: 8089
  • Country: de
  • A qualified hobbyist ;)
Re: The BIG EEVblog Server Fire
« Reply #60 on: April 08, 2021, 01:21:06 pm »
It would be nice if WebNX added a large NAS with its own power management in a shipping container at both their locations, with high bandwidth connectivity into their data centers.   Its only a bit over 600 miles as the crow flies between their locations, (729 miles by road, est. 10.5H driving time), so if they had another extended outage, the whole NAS could be shipped to their other location to facilitate getting fall-back servers online without the bandwidth implications of either uploading from off-site backups, or live syncing over a significant geographical distance.  They'd also need a priority standby contract with a local shipping company at each end to provide a self-loading container truck and two drivers with N hours notice 24/7.

First off, SAN, not NAS. Secondly, such an off-site backup requires fat pipes anyway for read and write, e.g. 100 Gbps Ethernet. So moving the SAN around won't speed up things. Actually it would cause a delay by the transport and also would add the risk of being damaged during transport, by a traffic accident for example.
« Last Edit: April 08, 2021, 01:24:06 pm by madires »
 

Offline Ultrapurple

  • Super Contributor
  • ***
  • Posts: 1027
  • Country: gb
  • Just zis guy, you know?
    • Therm-App Users on Flickr
Re: The BIG EEVblog Server Fire
« Reply #61 on: April 08, 2021, 03:26:44 pm »
Never underestimate the bandwidth of a station wagon full of tapes hurtling down the highway.

— Andrew S Tanenbaum, 1989
Rubber bands bridge the gap between WD40 and duct tape.
 
The following users thanked this post: Ed.Kloonk, Ian.M

Offline Microdoser

  • Frequent Contributor
  • **
  • Posts: 423
  • Country: gb
Re: The BIG EEVblog Server Fire
« Reply #62 on: April 08, 2021, 03:33:27 pm »
This has made me consider my own data safety and the importance of having an off-site backup of at leat the most critical things.
 

Offline Ultrapurple

  • Super Contributor
  • ***
  • Posts: 1027
  • Country: gb
  • Just zis guy, you know?
    • Therm-App Users on Flickr
Re: The BIG EEVblog Server Fire
« Reply #63 on: April 08, 2021, 03:40:44 pm »
I have in front of me a 1TB microSD card, 15 x 11 x 1mm thick (fascinating hi-res X-Rays here). That works out at roughly 6GB per cubic millimetre.

Assuming we have a VW Passat (which claims 1780 litres of cargo space with the rear seats down), our modern equivalent of the station-wagon-full of tapes is potentially something like 1780 x (100 x 100 x 100) x 6GB, or around 10 exabytes (10x10^9 GB).

And yes I know we wouldn't get that capacity, they're slow to write to, and so on and so on, but it does make one think.
« Last Edit: April 08, 2021, 03:45:35 pm by Ultrapurple »
Rubber bands bridge the gap between WD40 and duct tape.
 

Online Ian.M

  • Super Contributor
  • ***
  • Posts: 13026
Re: The BIG EEVblog Server Fire
« Reply #64 on: April 08, 2021, 03:45:21 pm »
 

Offline madires

  • Super Contributor
  • ***
  • Posts: 8089
  • Country: de
  • A qualified hobbyist ;)
Re: The BIG EEVblog Server Fire
« Reply #65 on: April 08, 2021, 03:48:03 pm »
Never underestimate the bandwidth of a station wagon full of tapes hurtling down the highway.

— Andrew S Tanenbaum, 1989

Or the old fashioned sneakernet (https://en.wikipedia.org/wiki/Sneakernet) ;)

Anyhow, do your risk assessment!
 

Offline Ultrapurple

  • Super Contributor
  • ***
  • Posts: 1027
  • Country: gb
  • Just zis guy, you know?
    • Therm-App Users on Flickr
Re: The BIG EEVblog Server Fire
« Reply #66 on: April 08, 2021, 04:16:19 pm »
Never underestimate the bandwidth of a station wagon full of tapes hurtling down the highway.

— Andrew S Tanenbaum, 1989

Or the old fashioned sneakernet (https://en.wikipedia.org/wiki/Sneakernet) ;)

Yup, that was the source of my Tanenbaum quote.
Rubber bands bridge the gap between WD40 and duct tape.
 

Offline xmo

  • Regular Contributor
  • *
  • Posts: 193
  • Country: us
Re: The BIG EEVblog Server Fire
« Reply #67 on: April 08, 2021, 04:23:51 pm »
Day three without the forum....

TEA user:

"I have discovered something interesting."

I seem to be living with a woman!

Apparently, she is my wife.

She seems nice."
 
The following users thanked this post: schmitt trigger, Microdoser, duckduck

Offline tooki

  • Super Contributor
  • ***
  • Posts: 12447
  • Country: ch
Re: The BIG EEVblog Server Fire
« Reply #68 on: April 08, 2021, 04:31:22 pm »
Never underestimate the bandwidth of a station wagon full of tapes hurtling down the highway.

— Andrew S Tanenbaum, 1989
Yes, or of actual messenger pigeons!

With that said, the critical downside of the station wagon or pigeon is the latency! :P
 

Offline Microdoser

  • Frequent Contributor
  • **
  • Posts: 423
  • Country: gb
Re: The BIG EEVblog Server Fire
« Reply #69 on: April 08, 2021, 04:34:22 pm »
I have noticed the site, as we were told, seems a bit clunky and slow right now.

Still, gives me more time to fix up the I7 6700K 24GB Ram 256GB SSD that I found in the street fully working (except for the graphics card). It has a legitimate Windows 7 Ultimate OEM on it which I am currently getting Windows updates up to date in preparation to upgrade to Win 10 Pro
 

Offline Microdoser

  • Frequent Contributor
  • **
  • Posts: 423
  • Country: gb
Re: The BIG EEVblog Server Fire
« Reply #70 on: April 08, 2021, 04:35:58 pm »
Never underestimate the bandwidth of a station wagon full of tapes hurtling down the highway.

— Andrew S Tanenbaum, 1989
Yes, or of actual messenger pigeons!

With that said, the critical downside of the station wagon or pigeon is the latency! :P

Or the time someone put a CD on the back of a snail and sent it across a table and got better data transmission rates than using the LAN (at the time)
 
The following users thanked this post: tooki

Offline Ultrapurple

  • Super Contributor
  • ***
  • Posts: 1027
  • Country: gb
  • Just zis guy, you know?
    • Therm-App Users on Flickr
Re: The BIG EEVblog Server Fire
« Reply #71 on: April 08, 2021, 04:37:40 pm »
Never underestimate the bandwidth of a station wagon full of tapes hurtling down the highway.

— Andrew S Tanenbaum, 1989
Yes, or of actual messenger pigeons!

With that said, the critical downside of the station wagon or pigeon is the latency! :P

I'm sorry I'm dragging this so far off-topic; I promise to sit on the Naughty Step for a while and Think About What I've Done. But meanwhile, have a ponder about the effective latency in even, say, a thousand parallel, error-free, get-the-label-speed 10Gbps direct links for that amount of data. How many miles apart do your data centres have to be before it's quicker to send the data via wires than wheels?

And don't get me started on the effective data rate of a cargo plane worth of 6GB/mm3...

OK, I've arrived at the Naughty Step. Sitting in 3... 2... 1...
« Last Edit: April 08, 2021, 04:42:18 pm by Ultrapurple »
Rubber bands bridge the gap between WD40 and duct tape.
 

Offline madires

  • Super Contributor
  • ***
  • Posts: 8089
  • Country: de
  • A qualified hobbyist ;)
Re: The BIG EEVblog Server Fire
« Reply #72 on: April 08, 2021, 04:49:49 pm »
Yes, or of actual messenger pigeons!

With that said, the critical downside of the station wagon or pigeon is the latency! :P

... or a Tesla with autopilot turned on, or Mrs. Eagle looking for a nice meal to feed her children. If that was your only backup you'll have problem. >:D
 

Offline Hamster

  • Regular Contributor
  • *
  • Posts: 120
  • Country: us
Re: The BIG EEVblog Server Fire
« Reply #73 on: April 08, 2021, 04:54:52 pm »
New Article : https://datacenterfrontier.com/generator-catches-fire-causes-lengthy-data-center-outage-at-webnx/

Webhosting talk forum: https://www.webhostingtalk.com/showthread.php?t=1842301

---

I would abort continuing to host anything at this data center, here in Florida, most all data centers do NOT use water.. they use an FM200 Fire Suppression System, also, Generators are not co-located with the data center, they are usually detached just in case something like this happens, Generators due tend to go, and when the go, they go violently..  the worst part is, this data center probably had multiple gensets, covering the load, when one went down, it caused a cascade effect going down the line..  Fuel should of also been shut off and isolated, but it appears not?  There should of been 0 water damage inside the facilities, this clearly is some kind of failed engineering design of a building that probably should of not been designed to be a data center.

---

Another popular site ( pinside.com ) is still down.. they have recovered the data and restored it to a lower tiered server, but still down.. they have to "order' new hardware for them.
Arcade Board Repair Guru.  [ twitch: HammysHangout , youTube: Hammy Builds ]
 
The following users thanked this post: duckduck

Offline madires

  • Super Contributor
  • ***
  • Posts: 8089
  • Country: de
  • A qualified hobbyist ;)
Re: The BIG EEVblog Server Fire
« Reply #74 on: April 08, 2021, 05:05:20 pm »
And don't get me started on the effective data rate of a cargo plane worth of 6GB/mm3...

I'll take the bait. ;D So your data center #1 has burned down, nothing left, no network connectivity, no servers, no power. But you have a backup in data center #2. To which servers do you want to restore the backup?
 


Share me

Digg  Facebook  SlashDot  Delicious  Technorati  Twitter  Google  Yahoo
Smf