Hello all, I need some help to clear up a question which was asked about two pin inverters and adding an earth

If I have an inverter 12v to 240v which only supplies a positive and neutral output, how would someone add an earth to the output so they can install a RCD.

I was thinking like industry installation the earth will be connected to the neutral at the output end next to the inverter and then an RCD will be fitted live and neutral further down. I cant see any reason this would not work.

Would it make any problem grounding this earth to a vehicle chassis with the 12v negative also grounded to the vehicle chassis
 

Offline BrokenYugo

  • Super Contributor
  • ***
  • Posts: 1188
  • Country: us
Re: Adding earth and RCD to two pin inverter
« Reply #1 on: August 08, 2021, 05:04:33 pm »
A RCD/GFCI doesn't need an earth connection to function, they work by checking for a current imbalance between live and neutral, doesn't matter if the leak is to earth or elsewhere. In fact in the USA where we often build them into the socket it's permitted to install one in an old 2 wire installation with no earth connection, works great.
 

Offline Zero999

  • Super Contributor
  • ***
  • Posts: 19841
  • Country: gb
  • 0999
Re: Adding earth and RCD to two pin inverter
« Reply #2 on: August 08, 2021, 05:21:42 pm »

A RCD/GFCI doesn't need an earth connection to function, they work by checking for a current imbalance between live and neutral, doesn't matter if the leak is to earth or elsewhere. In fact in the USA where we often build them into the socket it's permitted to install one in an old 2 wire installation with no earth connection, works great.
That's not true. An RCD or GFCI does need the mains to be earthed to work. It will work for appliances which aren't earthed, but it definitely requires a connection between the neural of the mains to ground.
Hello all, I need some help to clear up a question which was asked about two pin inverters and adding an earth

If I have an inverter 12v to 240v which only supplies a positive and neutral output, how would someone add an earth to the output so they can install a RCD.

I was thinking like industry installation the earth will be connected to the neutral at the output end next to the inverter and then an RCD will be fitted live and neutral further down. I cant see any reason this would not work.

Would it make any problem grounding this earth to a vehicle chassis with the 12v negative also grounded to the vehicle chassis
The neutral should be connected to the chassis, in order for the RCD to work. The problem is the inverter will most likely consist of a DC:DC converter, with an H-bridge on the output to convert it to AC. The problem is, the DC:DC converter might not be isolated, in which case, you need an RCD which will work with DC.
 

Offline David Hess

  • Super Contributor
  • ***
  • Posts: 17065
  • Country: us
  • DavidH
Re: Adding earth and RCD to two pin inverter
« Reply #3 on: August 08, 2021, 05:57:00 pm »
A RCD/GFCI doesn't need an earth connection to function, they work by checking for a current imbalance between live and neutral, doesn't matter if the leak is to earth or elsewhere. In fact in the USA where we often build them into the socket it's permitted to install one in an old 2 wire installation with no earth connection, works great.

That's not true. An RCD or GFCI does need the mains to be earthed to work. It will work for appliances which aren't earthed, but it definitely requires a connection between the neural of the mains to ground.

It needs a conductive path between the mains and earth for a failure to occur to be detected, which means that it works fine without it because then there is no possible failure.  An imbalance between the hot and neutral currents means that there is a third path, which could be through earth ground or not, and that is what the RCD or GFCI detects.

If you had an RCD or GFCI installed after an isolation transformer, then it would detect a simultaneous ground fault and failure of the isolation transformer.  Some isolation systems monitor the voltage across the isolation transformer to detect failure so they can disconnect when conditions become hazardous.
 

Offline motorhomerTopic starter

  • Contributor
  • Posts: 39
  • Country: gb
Re: Adding earth and RCD to two pin inverter
« Reply #4 on: August 08, 2021, 06:37:06 pm »
Ok so I understand how the RCD works. With out an earth the only way it will trip is a leak from positive back to UK inverter without going through the RCD. So back to neutral side. With the earth it's more likely to go back this route and trip quicker

So my theory is ok to connect the earth to neutral at the inverter output and then the RCD

Not sure about any issues connecting this earth to chassis found some info where it's adviced to do this.
 

Offline motorhomerTopic starter

  • Contributor
  • Posts: 39
  • Country: gb
Re: Adding earth and RCD to two pin inverter
« Reply #5 on: August 08, 2021, 06:39:44 pm »
So agree then nuatral to chassis which will be the earth return. Not sure why it would need to be DC one when the output is AC.
 

Offline Zero999

  • Super Contributor
  • ***
  • Posts: 19841
  • Country: gb
  • 0999
Re: Adding earth and RCD to two pin inverter
« Reply #6 on: August 08, 2021, 09:24:10 pm »
A RCD/GFCI doesn't need an earth connection to function, they work by checking for a current imbalance between live and neutral, doesn't matter if the leak is to earth or elsewhere. In fact in the USA where we often build them into the socket it's permitted to install one in an old 2 wire installation with no earth connection, works great.

That's not true. An RCD or GFCI does need the mains to be earthed to work. It will work for appliances which aren't earthed, but it definitely requires a connection between the neural of the mains to ground.

It needs a conductive path between the mains and earth for a failure to occur to be detected, which means that it works fine without it because then there is no possible failure.  An imbalance between the hot and neutral currents means that there is a third path, which could be through earth ground or not, and that is what the RCD or GFCI detects.

If you had an RCD or GFCI installed after an isolation transformer, then it would detect a simultaneous ground fault and failure of the isolation transformer.  Some isolation systems monitor the voltage across the isolation transformer to detect failure so they can disconnect when conditions become hazardous.
You've missed the point. Without the secondary of the inverter connected to earth, the RCD will not detect a live to earth fault. To be more specific, the neutral needs to be earthed before the RCD, in order for it to work. If it's earthed after the RCD, it will provide no protection.

Ok so I understand how the RCD works. With out an earth the only way it will trip is a leak from positive back to UK inverter without going through the RCD. So back to neutral side. With the earth it's more likely to go back this route and trip quicker

So my theory is ok to connect the earth to neutral at the inverter output and then the RCD

Not sure about any issues connecting this earth to chassis found some info where it's adviced to do this.
You mean phase, or live, not positive, because it's AC.

In a car, the chassis is considered to be earth. Some inverters have the neutral connected to earth, some don't. The easiest way to find out is to check the continuity between the neutral and the 0V connection to the inverter. This should obviously be done with the power off.
 

Offline motorhomerTopic starter

  • Contributor
  • Posts: 39
  • Country: gb
Re: Adding earth and RCD to two pin inverter
« Reply #7 on: August 09, 2021, 06:16:17 pm »
Ok so I did get wrong terminology,

I agree the RCD will not work without the earth and the way I was going to overcome this was to connect the neutral direct from the inverter to an earth wire giving the three live earth and neutral connections. This will then pass through an RCD and to any appliance so the appliance will have an earth. I do not see any issue with this at first until you get a live conductor short out to the vehicle bodywork then there is a potential lethal voltage on the bodywork which will not be detected until a person touching this body work then touched the earthed appliance.

To over come this connecting the earth/neutral connection to the chassis will make it all safe, but then someone pointed out some inverters are not true isolation between input and output so when the neutral switches to high it will be a short to the battery negative.

On more expensive inverters there will be an isolation like a transformer I expect. So cheap inverters are either to be kept with no earth to make them safe or do not use them
 

Offline james_s

  • Super Contributor
  • ***
  • Posts: 21611
  • Country: us
Re: Adding earth and RCD to two pin inverter
« Reply #8 on: August 09, 2021, 07:32:31 pm »
This is one case where it probably makes more sense to refer to "ground" rather than "earth". In a rolling vehicle there is no connection to earth unless you're plugged into shore power. The vehicle chassis is ground but it isn't earth ground.
 

Offline motorhomerTopic starter

  • Contributor
  • Posts: 39
  • Country: gb
Re: Adding earth and RCD to two pin inverter
« Reply #9 on: August 09, 2021, 07:33:33 pm »
Ok thanks for that
 

Offline motorhomerTopic starter

  • Contributor
  • Posts: 39
  • Country: gb
Re: Adding earth and RCD to two pin inverter
« Reply #10 on: August 09, 2021, 07:45:49 pm »
So the RVDs look good and a good way to protect on this system. I assume these are not on sale in the UK. Has anyone fitted these
 

Offline Zero999

  • Super Contributor
  • ***
  • Posts: 19841
  • Country: gb
  • 0999
Re: Adding earth and RCD to two pin inverter
« Reply #11 on: August 09, 2021, 09:44:20 pm »
This is one case where it probably makes more sense to refer to "ground" rather than "earth". In a rolling vehicle there is no connection to earth unless you're plugged into shore power. The vehicle chassis is ground but it isn't earth ground.
Ground also implies earth to me. They are different words for the same thing. Ground, is more commonly used in the US and Canada and earth, in the UK and Australia. For example, in the UK modern cars are referred to has having a negative, rather than positive earth, as was the case for some vintage models.

If you really want to be unambiguous, you should refer to 0V, common, or chassis, rather than earth, or ground.

Ok so I did get wrong terminology,

I agree the RCD will not work without the earth and the way I was going to overcome this was to connect the neutral direct from the inverter to an earth wire giving the three live earth and neutral connections. This will then pass through an RCD and to any appliance so the appliance will have an earth. I do not see any issue with this at first until you get a live conductor short out to the vehicle bodywork then there is a potential lethal voltage on the bodywork which will not be detected until a person touching this body work then touched the earthed appliance.

To over come this connecting the earth/neutral connection to the chassis will make it all safe, but then someone pointed out some inverters are not true isolation between input and output so when the neutral switches to high it will be a short to the battery negative.

On more expensive inverters there will be an isolation like a transformer I expect. So cheap inverters are either to be kept with no earth to make them safe or do not use them
The problem is, it's possible the output from the inverter floats, at a DC voltage, with respect to earth/the 0V input terminal, which would result in a short circuit, if you connected the neutral to the chassis.
 

Offline motorhomerTopic starter

  • Contributor
  • Posts: 39
  • Country: gb
Re: Adding earth and RCD to two pin inverter
« Reply #12 on: August 09, 2021, 10:17:18 pm »
Quote
The problem is, it's possible the output from the inverter floats, at a DC voltage, with respect to earth/the 0V input terminal, which would result in a short circuit, if you connected the neutral to the chassis.

Thanks I realise the problem with this if the converter does not have an isolating output. We use large inverters at work but they have isolating transformers on the output stage so the negative can and is connected to a chassis for a earth return.

I expect this is the problem with buying cheap inverters. The guy that was asking be the question is now considering buying a different inverter which supplies the correct protection circuits and a earth point
 


Share me