Author Topic: DMM Hz wrong? Or equipment under test problem  (Read 468 times)

bte and 1 Guest are viewing this topic.

Offline horse_ebookmarkletTopic starter

  • Contributor
  • Posts: 14
  • Country: us
DMM Hz wrong? Or equipment under test problem
« on: July 17, 2024, 09:30:12 pm »
Hey,
I am getting a reading I don't understand on my ExTech EX330, 10 years old, but fresh batteries.
I have this old junk generator (not gen inverter!) 130232-1839-01 I've been fixing. Its loud and heavy, but it was free.
I'm trying to set the unloaded frequency to ~62Hz, but my meter is giving me inconsistent readings. Sometimes they're believable (off by a few Hz), sometimes its off in the weeds (double the frequency)

In the below video you see:
  • Me turn the meter on
  • Meter reads ~55Hz for a bit
  • Meter jumps to ~160Hz
  • Me turn the meter off, then back on
  • Meter reads ~55Hz for a bit
  • Meter jumps to ~160Hz

Since it gives a plausible answer when first powered on (55Hz) and the motor speed is not varying, I think my measurement is suspect.
Whats my source of error here? Generator kicking off such noisy power the meter is getting confused?

https://www.youtube.com/shorts/m4hFRWxauQg
 

Offline BeBuLamar

  • Super Contributor
  • ***
  • Posts: 1258
  • Country: us
Re: DMM Hz wrong? Or equipment under test problem
« Reply #1 on: July 17, 2024, 10:05:39 pm »
I think your generator generates a lot of harmonic and the meter is picking up on the harmonic.
 

Offline RoGeorge

  • Super Contributor
  • ***
  • Posts: 6477
  • Country: ro
Re: DMM Hz wrong? Or equipment under test problem
« Reply #2 on: July 18, 2024, 09:48:33 am »
My guess would be that's either a bad DMM, or the generator is putting out a waveform with lots of 3rd harmonics (probably without any load, the generated fvoltage goes too high, then some other circuit is limiting to keep the AC at 110V, resulting a square waveform instead of sinusuoidal AC - square waveforms have a lot's of odd harmonics, the 3rd one is almost as big as the main frequency).

I would try adding a few incandescent lightbulbs as a purely resistive load (so not LEDs or CFL lights), then try to measure again, to see if adding some resistive load to the generator will make the frequency measure a constant 60Hz.

If not interested in extra testing, don't bother connecting light bulbs, just let it be and divide the number on the DMM by 3, so adjust the motor for 62x3 = 186Hz on the DMM without load.
« Last Edit: July 18, 2024, 09:52:43 am by RoGeorge »
 

Offline BrokenYugo

  • Super Contributor
  • ***
  • Posts: 1153
  • Country: us
Re: DMM Hz wrong? Or equipment under test problem
« Reply #3 on: July 18, 2024, 01:09:16 pm »
Number leads to a Briggs engine, assuming typical 3-5kW chinese import style genset and 60Hz power.

Hz is heavily tied to RPM, a 2 pole genset should have a unloaded high idle around 3700-3750 for about 62hz (max) no load, right on 60.0 around 50% load (space heaters work well, know how the outlets are wired so you can balance the loads between the two 120 windings) the engine would experience connecting rod failure or valve float before it spun fast enough to make 160Hz, so this has to be the typically dirty waveform they put out confusing the meter.

I usually use a killawatt or similar for generator governor setup, no annoying auto off issues. My AN870 (only DMM I have that does frequency) also has never failed to give me a sane reading as far as I can remember, that said this isn't something I do often.

Also, remember, these things are far from perfect and absolutely not high precision machines. Don't chase a perfect reading, just get it close enough, verify the no load speed isn't too high, and confirm the governor behavior is stable when you put a big load on it. Run a good tough oil in it for reliability, I prefer 5w40 diesel truck oil. Always flip the fuel valve off and run it dry before storing.
« Last Edit: July 18, 2024, 01:25:22 pm by BrokenYugo »
 

Online Zero999

  • Super Contributor
  • ***
  • Posts: 19682
  • Country: gb
  • 0999
Re: DMM Hz wrong? Or equipment under test problem
« Reply #4 on: July 18, 2024, 03:34:19 pm »
Use an oscilloscope and a small mains transformer to look at the output waveform.
 

Offline schmitt trigger

  • Super Contributor
  • ***
  • Posts: 2281
  • Country: mx
Re: DMM Hz wrong? Or equipment under test problem
« Reply #5 on: July 18, 2024, 04:17:08 pm »
Very likely a heavily distorted waveform.
The only way to know for sure is to follow Zero999’s suggestion.

If you don’t own a scope, borrow one.
 

Offline Vovk_Z

  • Super Contributor
  • ***
  • Posts: 1449
  • Country: ua
Re: DMM Hz wrong? Or equipment under test problem
« Reply #6 on: July 19, 2024, 04:06:53 pm »
All small generators general very unpure wavevform with a lot of 3, 5 and other higher harmonics.
 

Offline BeBuLamar

  • Super Contributor
  • ***
  • Posts: 1258
  • Country: us
Re: DMM Hz wrong? Or equipment under test problem
« Reply #7 on: July 19, 2024, 04:24:13 pm »
Out of curiousity I create a 60Hz sine wave with 80% third harmonic distortion using AWG and measured the frequency with the Fluke 87V. I couldn't get the meter to read the harmonic. It still read 60Hz.
 

Online TimFox

  • Super Contributor
  • ***
  • Posts: 8085
  • Country: us
  • Retired, now restoring antique test equipment
Re: DMM Hz wrong? Or equipment under test problem
« Reply #8 on: July 19, 2024, 08:17:51 pm »
The harmonic content of the dirty generator output may include "spikes" at twice the fundamental frequency, which would trick most counters into measuring that second harmonic frequency.
 

Offline schmitt trigger

  • Super Contributor
  • ***
  • Posts: 2281
  • Country: mx
Re: DMM Hz wrong? Or equipment under test problem
« Reply #9 on: July 20, 2024, 01:22:21 pm »
To the TS:
Unless the waveform is actually viewed with a scope, anything that is mentioned here will be speculation.
« Last Edit: July 20, 2024, 01:24:58 pm by schmitt trigger »
 