https://www.eia.gov/todayinenergy/detail.php?id=3990In 1 second the frequency rises .1hz and already generation is being taken offline, frequency continues to rise for 2 more seconds until generation matches load and the frequency begins to fall.
Its relatively easy to program an inverter to not be able to change its frequency that quickly, and reduce the power output in accordance with how quickly the frequency climbs, but slowly over a 10? second time frame, return to full power output regardless of frequency (within limits)
I suspect that such a simple algorithm would provide a lot of virtual inertia. Not enough to hold the grid up, but make it easier on the grid operators to give them more time to shut down generation when the frequency rises because the load is falling.
This comes at very small decreased revenue by the solar farms. yes someone has to pay.
Using the solar farms to provide reactive vars.. only helps if the utility operators command it to. when the power demand changes, the power factor can go either way, leading or lagging..
you don't know this ahead of time. IanB's idea that generators sink power is not correct. what happens is the prime generators are driven by machines that produce torque, the generator will always spin faster if you decrease the load, and they will always follow the grid frequency and slow down when the power demand increases.
The grid frequency rises when power in is greater than power out. What we need is more inertia in the system, and its a massive amount. Tf you read the prior link I posted, the UK wants 140 GJ of inertia. sounds like a lot, but when you are trying to balance out a system that needs to stay within 60.1 to 59.9hz, the energy miss match between what is pushed into and pulled out of the system between those frequencies is only
1/600th of 140 GJ. for a .1 second per second frequency increase or decrease. that's only 233MW miss match will result in a .1 hz frequency change per second.
I strongly suspect that the 40 ton flywheel mentioned by the prior link i posted, is storing 900MJ in the total inertia of the rotor at 1800 rpm for reasonable, 4 foot diameter, 40 tons worth of steel. it sounds like a lot but it really isn't, which explains why they need something like 100 of those added to the grid over the next decade.
Also I don't understand why Marco is talking about the zero crossing. It is true that most small solar farms are dumb inverters that follow the grid and wait .05 milliseconds each half cycle so they have anti-islanding capacity, but it doesn't matter much. The stored energy in the inductance of the power grid and the capacitors needed to offset that inductance, is pretty significant and it balances out most of the harmonics.
Consider the fact that 1GW sized transformers are inductive to the tune of 20%, and all of that inductance has to be canceled out with capacitors. It makes for a pretty good sized LC filter.