You only need a 3 phase incoming isolator, all others are single phase in a small office. 3 phase is good as you might want an aircon of more than 30 000 BTU which is almost invariably a 3 phase unit. Even allowing for a 10mm cable you have 20mm of copper, and a PE of 6mm, as opposed to the 3 phase one being 16mm of copper and a PE of 2.5mm. The internal wiring to the outlets and lighting plugs will still be 2.5mm and 1.5mm respectively.
This applies to South Africa, it is very similar in Australia for cable size, as this is dictated by allowable temperature rise in the cable when installed either bare in plaster, in conduit or in free air in a cable way in the building.