Yeah looks like the actual spec is +10/-6%, and preferred +6/-2%. Not sure where I got 1.1.
The domestic voltage spec is not the passive anti-islanding limit. I will discuss (to the best of my memory) Australia.
In terms of over voltage disconnection there are 2 fast limits and one 10 minute average limit.
>275V instantaneous - 200ms
>265V for 1s - 1s
>258V (adjustable) for 10 minutes - 3s
In terms of under voltage two limits plus specific ride through requirements
<180V for 10s - 1s
<70V for 1s - 1s
I don't remember ride through it's complicated.
In terms of frequency the disconnect range is 47hz and 52hz, with similar delays. Oh and 4hz/s rate of change of frequency.
(note that reconnection limits are different, and based on the grid spec).
The regions I've studied (Aus, Europe, North America) all have similar limit set ups, of course with different values.
Most regions also require active anti islanding (except UK). This requires the inverter to inject a disturbance signal into the grid and monitor the effects. This allows it to detect scenarios where, when an accidental islanded load matches the inverter generation, the voltage and frequency limits are still in range.