Still, did they give you any indication as to what type interface, (arduinos arent that far from plc's) basic models tend to come with only digital in and digital out, and usually some bus connector, commonly HART, PROFIBUS, SCADA, and a few others of that genre,
aftermarket interfaces are more commonly
- A/D: Current 4-20mA commonly, but some 7-15mA stuff is still flaoting around though rare, if so allow for 3-21mA, but present some way of limiting it to 4-20 (some plc's go into alarm)
: Voltage 1-5V commonly, with 2-10 and 7-15V stuff floating around, if 1-5, allow for 0.75 to 5.125, and like current build in the option of a limit,
: Milli-volt, depending on the type of thermocouple, it can be from about -100mV to +100mV, and these values i have not confirmed,
- D/A: same as above, but there are some more fancy things like Variable speed drives that can be included under these,
- A/A: is almost non existant, as a 250 ohm resistor can usually convert between the 2 common types, though thermocoule to current or voltage is somewhat common
- D/D: this is where i suspect you may be playing with, as its not to uncommon for plants to want to control a few different types of units that may use different protocols off the one control system,
also be aware, most plc gear is rated for 48V on any input and sometimes output, with alarm options in software for nearly anything,