Author Topic: The oscilloscope probe is connected to the ground but the signal is AC?  (Read 1894 times)

0 Members and 2 Guests are viewing this topic.

Offline mike bubaTopic starter

  • Contributor
  • Posts: 41
  • Country: gb
Hi, please help me to understand what am I seeing on the oscilloscope ??? ... and how to see 0 volts?

I would like to measure a common-mode voltage, i.e. voltage between load neutral and the ground. My setup is shown in the figure below:
1620301-0

However, when I connect only one input of the differential probe to the GND (PE), I see ~ 50 Vpeak, 50 Hz signal on the oscilloscope. The same is if I connect to N (load neutral point) and GND (PE). In both cases, there is no DC voltage at the inverter input.
1620307-1

The multimeter shows zero volts between N and GND.

When I run the inverter, I see this AC voltage superimposed to the common-mode voltage:
1620313-2

I tried with two differential probes: Pico TA057 and Micsig DP10013

« Last Edit: October 22, 2022, 04:06:26 pm by mike buba »
 

Offline jonpaul

  • Super Contributor
  • ***
  • Posts: 3596
  • Country: fr
  • EE for 55 yrs
Re: The oscilloscope probe is connected to the ground but the signal is AC?
« Reply #1 on: October 22, 2022, 10:53:33 pm »
schematic of setup?

no idea what the connections are probe, scope, mains.

j
The Internet Dinosaur
 

Offline nightfire

  • Frequent Contributor
  • **
  • Posts: 587
  • Country: de
Re: The oscilloscope probe is connected to the ground but the signal is AC?
« Reply #2 on: October 23, 2022, 03:12:48 am »
Depending on the mains setup in your area, there is very well the chance that you have a TN network, meaning that usually the N is connected to PE in the main distribution cabinet in your house.
Therefore the voltage between N and PE should (at least in theory) be close to Zero.
 

Offline bdunham7

  • Super Contributor
  • ***
  • Posts: 8010
  • Country: us
Re: The oscilloscope probe is connected to the ground but the signal is AC?
« Reply #3 on: October 23, 2022, 03:18:48 am »
Where is your oscilloscope grounded?  Is there voltage between your PE and the oscilloscope ground?  (I hope not...)
A 3.5 digit 4.5 digit 5 digit 5.5 digit 6.5 digit 7.5 digit DMM is good enough for most people.
 

Online Gyro

  • Super Contributor
  • ***
  • Posts: 10026
  • Country: gb
Re: The oscilloscope probe is connected to the ground but the signal is AC?
« Reply #4 on: October 23, 2022, 08:51:26 am »
According to the OP's diagram, the scope is on an isolation transformer.
Best Regards, Chris
 

Offline hexreader

  • Frequent Contributor
  • **
  • Posts: 269
  • Country: england
Re: The oscilloscope probe is connected to the ground but the signal is AC?
« Reply #5 on: October 23, 2022, 09:38:33 am »
In the UK, ground is typically derived from a metal stake driven into the mud close to the house

Neutral is derived from a ground connection at the electricity sub-station.

It is perfectly normal for up to a few volts AC to be measured between ground and neutral at a wall socket in UK

Right now I have 300mV RMS ground to neutral

At my last house I have measured 8V peak-to-peak (3V RMS)

Each domestic house is supplied with a single phase of a three phase supply, so neutral voltage is likely to vary as the loading imbalance between phases varies

I wouldn't like to guess as to what effects the OPs inverter is causing to the ground and neutral voltages
« Last Edit: October 23, 2022, 10:05:45 am by hexreader »
 

Offline bdunham7

  • Super Contributor
  • ***
  • Posts: 8010
  • Country: us
Re: The oscilloscope probe is connected to the ground but the signal is AC?
« Reply #6 on: October 23, 2022, 02:56:26 pm »
According to the OP's diagram, the scope is on an isolation transformer.

But that doesn't answer my question either way as isolation transformers typically pass the PE through.  If he is floating the scope ground (why!?!) then I'd ask about the power supply for the differential probe as the Y-caps from that may be putting that voltage on the floated components.  And this is a good example of the pitfalls of HV differential probes--they are not isolated

A 3.5 digit 4.5 digit 5 digit 5.5 digit 6.5 digit 7.5 digit DMM is good enough for most people.
 

Offline mike bubaTopic starter

  • Contributor
  • Posts: 41
  • Country: gb
Re: The oscilloscope probe is connected to the ground but the signal is AC?
« Reply #7 on: October 30, 2022, 04:24:10 pm »
If he is floating the scope ground (why!?!)


I've always been told to flote the oscilloscope ground, especially if I'm
  • measuring with multiple grounds and I'm not sure if they are connected
  • measuring voltage above 50 V
  • combining low voltage (e.g. using probe x100) and PCB measurements
Although now reading about it, it says
Isolation Transformers WARNING! This Is An Unsafe And Dangerous Practice And Should Never Be Done!.

My oscilloscope channels are
  • Ch1: x100 votlage (+) to neutral, (-) to earth -> common mode voltage
  • Ch2: differetina probe (+) to phase A, (-) to phase B
  • Ch3: differetina probe (+) to phase C, (-) to neutral,
  • Ch4: current probe
Oscillogram: 1627519-0



I am trying to understand where this AC signal is coming from and how to eliminate it because I am trying to measure common mode voltage, i.e. voltage between load neutral and earth. I have made the connection as shown in this article, Fig. 1, and would expect to measure similar common mode voltage,
Fig. 4. Even this article and this Fig. 12 show Vcm without AC signal superimposed.
When simulating, I get 0 volts between the neutral point and the earth, but in real measurements, there is an AC signal superimposed (see 1627519-1, Ch1)
« Last Edit: October 30, 2022, 04:57:40 pm by mike buba »
 

Online themadhippy

  • Super Contributor
  • ***
  • Posts: 3017
  • Country: gb
Re: The oscilloscope probe is connected to the ground but the signal is AC?
« Reply #8 on: October 30, 2022, 04:35:31 pm »
Quote
In the UK, ground is typically derived from a metal stake driven into the mud close to the house
you can only guarantee that on a TT system,  TNC-S and TNS  system the spike to earth maybe some distance away
 

Offline EPAIII

  • Super Contributor
  • ***
  • Posts: 1156
  • Country: us
Re: The oscilloscope probe is connected to the ground but the signal is AC?
« Reply #9 on: October 31, 2022, 09:57:10 am »
Just taking a stab at it.

First, in attachment 2 you are using a differential probe but only one of the two probe leads is attached to anything. The other one is, unassumingly, just floating. It is not unusual for a high impedance, floating input to pick up some radiation from the local power lines. 50 or 60 Hertz RF is floating all around our planet. I have seen this many times when a scope probe is not connected. If you connect that probe to it's common, either directly or with a low value resistor, it should disappear.

Likewise, in attachment 3 I see what looks like the power line frequency and, perhaps, what is the switching frequency of the inverter. Neither of these is surprising at the low, milli-Volt levels of that trace.

In both cases you are seeing only milli-Volts, for gosh sake!
« Last Edit: October 31, 2022, 10:02:06 am by EPAIII »
Paul A.  -   SE Texas
And if you look REAL close at an analog signal,
You will find that it has discrete steps.
 

Offline mike bubaTopic starter

  • Contributor
  • Posts: 41
  • Country: gb
Re: The oscilloscope probe is connected to the ground but the signal is AC?
« Reply #10 on: November 04, 2022, 12:12:34 pm »
In both cases you are seeing only milli-Volts
I am using a differential probe x500, so that translates into 100 V or more. Since I am not measuring anything between the natural and the ground with a multimeter, it seems I'm picking something.

Is there a way to eliminate that because it is affecting my other measurements as shown in the oscillograms, where that AC signal is added to a measured common-mode voltage?
« Last Edit: November 04, 2022, 12:50:04 pm by mike buba »
 

Online tggzzz

  • Super Contributor
  • ***
  • Posts: 20752
  • Country: gb
  • Numbers, not adjectives
    • Having fun doing more, with less
Re: The oscilloscope probe is connected to the ground but the signal is AC?
« Reply #11 on: November 04, 2022, 04:12:04 pm »
If he is floating the scope ground (why!?!)


I've always been told to flote the oscilloscope ground, especially if I'm
  • measuring with multiple grounds and I'm not sure if they are connected
  • measuring voltage above 50 V
  • combining low voltage (e.g. using probe x100) and PCB measurements

You have been told a lot of absolute rubbish in multiple ways. Some is dangerous rubbish. Is that perfectly clear?

I suggest you have look at the references in https://entertaininghacks.wordpress.com/library-2/scope-probe-reference-material/ Those will help you understand
  • why your techniques are dangerous - to your scope, to you, and to anybody else in the vicinity
  • what class of probe you need to use for different measurements

Hopefully you will then be able to stop using "cargo cult engineering".

EDIT: sorry I was so curt, but the way you have approached dangerous voltages put the wind up me.

There is no substitute for educating oneself from solid reliable sources of information; these are exceptionally easily accessible nowadays, unlike last century. Relying on yootoob vids from random kiddies, or people you chat to over the garden wall is a bad starting point.

The point is not to follow recipes blindly, but to understand why the recipes work. If you can't understand why a recipe works, then it might be that it is merely a "leg of lamb story"[1]. At the very least, compare and contrast multiple recipes for a range of very different sources to get a feel for which "cook" understands and which cook repeats what they do not understand. Deciding which is which is a key skill nowadays.

[1] Child: "Mummy, why do you cut off the end of the leg of lamb before roasting it"?
Mother: "That's the way granny did it when I was young".
Child: "But why?"
Mother: "Go and ask her!"
Child: "Granny, why did you cut off the end of the leg of lamb before roasting it"?
Grandmother, looks puzzled for 30s, then "Oh yes, because we had a small oven and I had to do that to get it to fit in".
« Last Edit: November 04, 2022, 07:04:42 pm by tggzzz »
There are lies, damned lies, statistics - and ADC/DAC specs.
Glider pilot's aphorism: "there is no substitute for span". Retort: "There is a substitute: skill+imagination. But you can buy span".
Having fun doing more, with less
 
The following users thanked this post: mike buba, nightfire