Author Topic: Problem with setting parameters VARISPEED V7 OmronV7 V7AZBOP7 1.1 KW  (Read 3213 times)
Offline IOANTopic starter
Hello,
I write the first time in this forum and hope resolve with your help my problem.
I bought (via EBAY) VARISPEED V7 OmronV7 V7AZBOP7 1.1 KW
 The seller was setting parameters for him use
 I have driving  (delta conexions)  3x220V/50Hz and current consummation it is 2,9 A. the drive use to mini lathe
 My Omron v 7 no good function  the drive have noise sound but no start , distance  drive ----varispeed  it is 6 meters.
not understanding setting  parameters for a good function.
 so, when command ,, RUN,, the driving start for 0,5 " secundes and stop
 the display information cod faulty OL3
Best regardes and please replay me.
IOAN
Offline AlfBaz
Re: Problem with setting parameters VARISPEED V7 OmronV7 V7AZBOP7 1.1 KW
« Reply #1 on: September 22, 2014, 10:14:17 am »
What are the motor specifications?
Looks like you are at the vfd's max kilowatt rating
Offline cs.dk
« Reply #2 on: September 23, 2014, 05:21:20 am »
From the manual:
OL3 (Overtorque detection)
Motor current exceeded the preset value in constant n098.
Overtorque detection level was exceeded because of increased leak current due to excessively long wiring.
Reduce the load, and increase the acceleration/deceleration time.
Refer to the paragraph of Carrier Frequency Selection (n080)14kHz max on page 93.
Check the wiring (increase of current caused by rare shortcircuit, etc.).
Whats the data on the motors nameplate?
Your acceleration time is 1,5 sec. Try increase is to ie. 5 sec. and see. (menu n19)
For a testrun you can disable the overtorque detection, set n096 to 0 (The feature is disabled when factory settings are loaded)
« Last Edit: September 23, 2014, 05:30:45 am by cs.dk »
