Author Topic: Low voltage cut-off at Mains level  (Read 7006 times)

0 Members and 1 Guest are viewing this topic.

Offline tribatTopic starter

  • Contributor
  • Posts: 19
Low voltage cut-off at Mains level
« on: January 25, 2011, 02:31:34 pm »
My load is a 230VAC 28kohm (8.2mA) relay that on its own has a must drop-out voltage of 0.2Un which makes the relay open when voltage goes under 50VAC. But I need the relay to open much sooner, say when voltage goes below 200VAC. Is there a simple circuit I could use to achieve this?
 

Offline Kiriakos-GR

  • Super Contributor
  • ***
  • !
  • Posts: 3525
  • Country: gr
  • User is banned.
    • Honda AX-1 rebuild
Re: Low voltage cut-off at Mains level
« Reply #1 on: January 25, 2011, 03:35:08 pm »
My load is a 230VAC 28kohm (8.2mA) relay that on its own has a must drop-out voltage of 0.2Un which makes the relay open when voltage goes under 50VAC. But I need the relay to open much sooner, say when voltage goes below 200VAC. Is there a simple circuit I could use to achieve this?

Please define the word " simple " .  :)
 

Offline FreeThinker

  • Frequent Contributor
  • **
  • Posts: 791
  • Country: england
  • Truth through Thought
Re: Low voltage cut-off at Mains level
« Reply #2 on: January 25, 2011, 04:17:52 pm »
You could try wiring a resistor across a nc contact in series with the coil and playing with the spring tension of the moving contact block. When switched on the full 230v is applied via the nc contact which then opens and holds the coil just above the desired dropout voltage, may work never tried it but the theory is sound.Some experimentation will be required and current capacity could (almost certainly will) be reduced.Also no two coils will be the same so some variation in the operating point is to be expected.
Machines were mice and Men were lions once upon a time, but now that it's the opposite it's twice upon a time.
MOONDOG
 

Online Zero999

  • Super Contributor
  • ***
  • Posts: 19904
  • Country: gb
  • 0999
Re: Low voltage cut-off at Mains level
« Reply #3 on: January 25, 2011, 06:35:47 pm »
The easiest way is to buy a low voltage protection relay which will do what you want.
 

Offline JohnS_AZ

  • Frequent Contributor
  • **
  • Posts: 499
  • Country: us
    • About.me
Re: Low voltage cut-off at Mains level
« Reply #4 on: January 25, 2011, 06:48:24 pm »
I'm either at my bench, here, or on PokerStars.
 

Offline tribatTopic starter

  • Contributor
  • Posts: 19
Re: Low voltage cut-off at Mains level
« Reply #5 on: January 26, 2011, 01:11:29 am »
The easiest way is to buy a low voltage protection relay which will do what you want.
Where could I get one?

You could try wiring a resistor across a nc contact in series with the coil and playing with the spring tension of the moving contact block. When switched on the full 230v is applied via the nc contact which then opens and holds the coil just above the desired dropout voltage, may work never tried it but the theory is sound.Some experimentation will be required and current capacity could (almost certainly will) be reduced.Also no two coils will be the same so some variation in the operating point is to be expected.
Problem with that is the relay is not guaranteed to hold once the voltage goes under 0.8Un. So keeping it at say 0.3Un under normal used would probably mean a little vibration might make it lose contact.

You might get some ideas from here ...

http://www.brighthub.com/engineering/electrical/articles/68396.aspx


Those circuits use a DC relay that needs a big bulky transformer to go with it, I wonder if there's a way to do this without a transformer.
 

Offline FreeThinker

  • Frequent Contributor
  • **
  • Posts: 791
  • Country: england
  • Truth through Thought
Re: Low voltage cut-off at Mains level
« Reply #6 on: January 26, 2011, 07:56:54 am »

Problem with that is the relay is not guaranteed to hold once the voltage goes under 0.8Un. So keeping it at say 0.3Un under normal used would probably mean a little vibration might make it lose contact.

Exactly my point about the reduced current rating.Reducing the spring tension will help (while making the vibration issues worse) but without going to voltage sense relays or voltage monitoring circuits you are very limited.
Machines were mice and Men were lions once upon a time, but now that it's the opposite it's twice upon a time.
MOONDOG
 

Online Zero999

  • Super Contributor
  • ***
  • Posts: 19904
  • Country: gb
  • 0999
Re: Low voltage cut-off at Mains level
« Reply #7 on: January 26, 2011, 10:20:37 pm »
Where could I get one?
It's a standard part which is normally used to protect AC motors which can stall and cook if the voltage falls too low.

Here are some examples:
http://www.schurterinc.com/Products/Circuit-Breakers/Undervoltage-Protection
http://www.schurterinc.com/en/schurter/link/pdf/datasheet_PG_Undervoltage_Protection_040191010000008762

Although these might not be suitable for you since they operate when the voltage drops to 35% of the rated value which is 84V.

I think you'll have difficulty finding something which operates at 200V, you might be able to get 180V.

What voltage do you want it to turn back on at? Do you want manual or automatic release?

If you go for the home made option, you can get some pretty small transformers. I'd probably use a small <3VA PCB mounted transformer, an LM311 and a suitable voltage reference. I'll post a schematic and suggest some parts, if you're interested.
 

Offline tribatTopic starter

  • Contributor
  • Posts: 19
Re: Low voltage cut-off at Mains level
« Reply #8 on: January 28, 2011, 04:05:59 am »
Where could I get one?
It's a standard part which is normally used to protect AC motors which can stall and cook if the voltage falls too low.

Here are some examples:
http://www.schurterinc.com/Products/Circuit-Breakers/Undervoltage-Protection
http://www.schurterinc.com/en/schurter/link/pdf/datasheet_PG_Undervoltage_Protection_040191010000008762

Although these might not be suitable for you since they operate when the voltage drops to 35% of the rated value which is 84V.

I think you'll have difficulty finding something which operates at 200V, you might be able to get 180V.

What voltage do you want it to turn back on at? Do you want manual or automatic release?

If you go for the home made option, you can get some pretty small transformers. I'd probably use a small <3VA PCB mounted transformer, an LM311 and a suitable voltage reference. I'll post a schematic and suggest some parts, if you're interested.
Your right, a small PCB transformer would be pretty compact, but can it deliver enough current to power the voltage monitor circuit and a relay? A schematic would be really helpful!
 

Online Zero999

  • Super Contributor
  • ***
  • Posts: 19904
  • Country: gb
  • 0999
Re: Low voltage cut-off at Mains level
« Reply #9 on: January 28, 2011, 06:39:36 pm »
That depends on how large the relay is which is determined by the voltage/current it needs to switch.

Is the load capacitive, inductive or resistive?

It's possible you could do away with the relay and use a TRIAC which would mean you could use a small capacitive power supply, rather than a transformer.
 

Offline tribatTopic starter

  • Contributor
  • Posts: 19
Re: Low voltage cut-off at Mains level
« Reply #10 on: January 28, 2011, 10:19:12 pm »
That depends on how large the relay is which is determined by the voltage/current it needs to switch.

Is the load capacitive, inductive or resistive?

It's possible you could do away with the relay and use a TRIAC which would mean you could use a small capacitive power supply, rather than a transformer.
Load of the relay will be few computer PSU's (300W and 500W) and 3 x 12V 1A wall warts. I've never used a TRIAC so I wouldn't know if it could be used as a switch with a load like that.

I was thinking a relay like Finder 40.52.9.012 which has a 12VDC coil at 220ohm so it would need about 55mA. Also checked out the PCB transformers at my local electronics store and the 2.3VA 1 x 12V seemed like it might be a nice choice. It can delived 192 mA at 12V and has a voltage of 21.4V when not loaded.
 

Online Zero999

  • Super Contributor
  • ***
  • Posts: 19904
  • Country: gb
  • 0999
Re: Low voltage cut-off at Mains level
« Reply #11 on: January 29, 2011, 12:24:15 am »
Hmm can you get hold of a relay with a slightly higher resistance coil? I was going to suggest the LM311 but it's maximum output current is 50mA. It's not a big deal as you could use a buffer transistor, it's just a cleaner/cheaper design without one.  If not, it's possible to configure the LM311's output as an emitter follower so it drops a couple of volts which will reduce the relay voltage to 10V and current to 45mA but it's nor best practise.

I'll have a look tomorrow, I'm off to bed now.
 


Share me

Digg  Facebook  SlashDot  Delicious  Technorati  Twitter  Google  Yahoo
Smf