Yes I think a lot of confusion is in that the current referred to is the current of each phase, while the voltage given is the voltage between phases, this can lead to the incorrect calculation of 3xV*I when it is (1/1.7)*V*I
For example our new feed at work was referred to as 3x100A at 230V this gave the illusion of 69kW when in fact the current is shared out so it is (1/1.7)*300*230 which is 40kW. I'm not sure what the arrangement is and I don't know if there is one that is usually used.
if it 230V phase to neutral and 400V phase to phase and you have 100A on each phase you have 69kW
Exactly.
With star connection the voltage across the each load resistor is 230V, and the current through each load resistor is 100A. So the total power is 3 * 230 * 100 = 69kW.
With delta connection, the voltage across each load resistor is 398V, but the current through each load resistor can only be 58A, in order that the current through each phase does not exceed 100A. Total power is 3 * 398 * 58, i.e still 69kW.
The resistance of the load resistors must be 3x higher with delta connection than with star connection.
[ Btw, I'm considering only purely resistive load here, and only equal load on each phase. ]