Author Topic: Yaskawa/Omron V1000 VFD - Max. freq. locked  (Read 4909 times)
Offline cs.dkTopic starter
« on: June 16, 2013, 09:44:53 am »
I've installed/programmed several (used) Omron V1000s, but this one is giving me a headache. Max. frequency parameter is for some reason locked.
I started with Initialization;
Parameter O2-03 = 2 (Clear all)
Parameter A1-03 = 2220 (2 wire installation) (default when shipped)
But for some reason I can't edit E1-04 Max. frequency output.
Parameter A1-01 (Access Level) is set to full access.
Any ideas?
Offline edm68
Re: Yaskawa/Omron V1000 VFD - Max. freq. locked
« Reply #1 on: June 16, 2013, 07:18:45 pm »
I'm not familiar with the V1000, but on the Z1000 there is a parameter D2-01 that needs to be changed for the max frequency.  It needs to be stopped to change it.
Edit:
My mistake, it looks like for E1-04 thru E1-14 to be changed from their default values E1-03 needs to be set to F.
I was able to find a V1000 manual here:http://yaskawa.com/site/dmdrive.nsf/(DocID)/MHAL-7JSLMA/$File/SIEPC71060618.pdf
« Last Edit: June 16, 2013, 10:51:37 pm by edm68 »
« Reply #2 on: June 17, 2013, 07:34:25 pm »
You are absolutely right - Today I match all menues up with my other V1000's, and E1-03 was the only thing being different.. It is not mentioned in the quick-start guide, only in the full manual. Thanks alot for your reply :)
I just don't understand, I set the VFD to factory-default (i guess) - This parameter should be defaulted to?