I hope I am not starting a religious war with this ;D

Most induction motor wiring diagrams I have seen show the shorted ends of the windings simply left floating, on the grounds that phase voltages and motor windings ought to be symmetric, so the center point voltage is approximately zero anyway.

On the other hand, there appears to be a minority that insists that the star point should be connected to neutral in order to equalize small current imbalances that do occur.

Is this ever a serious concern? :-//
 

Offline Gyro

  • Super Contributor
  • ***
  • Posts: 9911
  • Country: gb
A good question. Possible factors I can think of...

- Does leaving the star point floating assist in 'balancing' the motor drive in the case of unequal phase voltages?
- Does it reduce the risk of motor damage if one phase drops out?
- How solid is the Neutral in a particular installation, sometimes it is weak and high resistance.
- On the other hand, err...
Best Regards, Chris
 

Offline capt bullshot

  • Super Contributor
  • ***
  • Posts: 3033
  • Country: de
    • Mostly useless stuff, but nice to have: wunderkis.de
Never seen the motors star point connected to anywhere.
It might work (meaning you should get away with "no magic smoke escape") if you do so with a regular 3ph mains, but never ever do this with a VFD (inverter) supplying the motor.
In a very special case, when one phase is open circuit, the motor might still be able to run if the start point is connected to neutral.
Safety devices hinder evolution
 

Offline mag_therm

  • Frequent Contributor
  • **
  • Posts: 783
  • Country: us
A title edit is suggested because "grounding" a circuit galvanically conected to a live source would be a code violation in most countries, however Magic correctly refers to connecting star (Y) to neutral in text of o.p.

Anyway:
A 3 wire connection is usually preferred because the 3 sources can handle the Negative sequence currents due to imbalance in the motor impedances or torque fluctuatiuons.
A 4th wire is not needed to do this balancing.
A 4th wire would/could have Zero sequence current in the neutral which is undesirable and might be higher if there is harmonic voltage distortion on the 3 phases which there usually is.

An industrial 3 phase distribution board will usually have a neutral bar to get single phase supplies , and it is desirable to reduce neutral currents to be as low as possible in the interest of reducing noise and balancing the loads on the incoming transformer.

With all the small phase supplies often having capacitor input  DC filters, the neutral currents have a 3rd harmonic component in which the contributions from the 3 phases add instead of cancel.

This is a reason why the Power Factor Correction type of small power supplies are needed.
 ( Like the one posted by Tim  yesterday : )
https://www.eevblog.com/forum/projects/power-factor-correction-discrete-control-circuit-(for-bcm)/ 
 
The following users thanked this post: magic

Offline Zero999

  • Super Contributor
  • ***
  • Posts: 19891
  • Country: gb
  • 0999
Connecting to neutral wouldn't hurt, but it won't make any difference either. Do not connect it to safety earth/ground. That's a bad idea and is against the safety regulations in most jurisdictions.
 

Online coppice

  • Super Contributor
  • ***
  • Posts: 9370
  • Country: gb
It depends. There is no point of grounding the star point of the actual motor. However, you often find there is something associated with the motor's wiring that is running from just one phase. For example the lighting on a three phase machine, or some electronic controller box.
 

Offline bdunham7

  • Super Contributor
  • ***
  • Posts: 8004
  • Country: us
At best it won't matter and at worst you'll get significant startup surges and 5th harmonics on the neutral which may disturb your control circuitry or even stuff in the rest of the building.  Or, if this connection is made inside of a unit which is later moved and connected to a corner-grounded delta service (a US thing only AFAIK, so no worries in Poland) you might have a bit of sparkles depending on what you do with the neutral.
A 3.5 digit 4.5 digit 5 digit 5.5 digit 6.5 digit 7.5 digit DMM is good enough for most people.
 

Online magicTopic starter

  • Super Contributor
  • ***
  • Posts: 7158
  • Country: pl
A title edit is suggested because "grounding" a circuit galvanically conected to a live source would be a code violation in most countries, however Magic correctly refers to connecting star (Y) to neutral in text of o.p.
Well, I meant grounding in the circuit theory sense. I had a character limit to fit this title in :P
Obviously, no one in his right mind advocates for connecting motor windings to safety earth.

But once in a while I run into handwavy arguments in favor of connecting it to neutral. For example here, and I frankly have no idea what they are talking about.
https://www.allaboutcircuits.com/textbook/alternating-current/chpt-10/three-phase-y-delta-configurations/
Quote
In a Y-connected system, there may or may not (Figure below) be a neutral wire attached at the junction point in the middle, although it certainly helps alleviate potential problems should one element of a three-phase load fail open, as discussed earlier.

And there are others, often internet forum users with low post count ::) who use language like "balance" without further elaboration on what exactly should go wrong if said "balance" is lacking.

I smell BS because wiring diagrams from manufacturers of motors and Y/Δ switches show the floating configuration, but I'm no expert on motors so maybe I'm missing something.
« Last Edit: September 10, 2022, 04:53:33 pm by magic »
 

Offline bdunham7

  • Super Contributor
  • ***
  • Posts: 8004
  • Country: us
Quote
In a Y-connected system, there may or may not (Figure below) be a neutral wire attached at the junction point in the middle, although it certainly helps alleviate potential problems should one element of a three-phase load fail open, as discussed earlier.

I can tell you with some certainty that in a system that has a neutral, having your large three-phase motors neutral connected will not prevent a flaming catastrophe if you lose a phase and your breakers don't promptly trip. Your single-phase loads that use the neutral for the lower voltage ((208/120 or 380/230 or similar) will be subject to huge surges as the neutral voltage goes crazy.  And yes, they're typically bonded to the ground at the service entrance in the US, but there is no breaker on the neutral! 
A 3.5 digit 4.5 digit 5 digit 5.5 digit 6.5 digit 7.5 digit DMM is good enough for most people.
 
The following users thanked this post: magic

Offline elekorsi

  • Regular Contributor
  • *
  • Posts: 112
  • Country: si
On 3ph motors you never connect the neutral. Never.
It's a balanced load

I am not saying that i had never saw one, but those cases were the result of "electricians" who got their eletrical degree from youtube and diy forums...
 

Offline fordem

  • Regular Contributor
  • *
  • Posts: 234
  • Country: gy
Connecting to neutral wouldn't hurt, but it won't make any difference either. Do not connect it to safety earth/ground. That's a bad idea and is against the safety regulations in most jurisdictions.

I'll just point out that many "jurisdictions" REQUIRE the neutral to be bonded to "safety earth/ground" at some point in the installation, typically the building entrance.
 

Online langwadt

  • Super Contributor
  • ***
  • Posts: 4684
  • Country: dk
Connecting to neutral wouldn't hurt, but it won't make any difference either. Do not connect it to safety earth/ground. That's a bad idea and is against the safety regulations in most jurisdictions.

I'll just point out that many "jurisdictions" REQUIRE the neutral to be bonded to "safety earth/ground" at some point in the installation, typically the building entrance.

and _only_ at that point
 
The following users thanked this post: Siwastaja

Offline elekorsi

  • Regular Contributor
  • *
  • Posts: 112
  • Country: si
Connecting to neutral wouldn't hurt, but it won't make any difference either. Do not connect it to safety earth/ground. That's a bad idea and is against the safety regulations in most jurisdictions.

I'll just point out that many "jurisdictions" REQUIRE the neutral to be bonded to "safety earth/ground" at some point in the installation, typically the building entrance.

Not really, combining Earth and neutral is only at the source, which in our case is the distribution transformer.
In TN-C system you get earth (PE) and neutral (N) combined, designated as PEN conductor from the distributor. Per IEC, PEN conductor is green/yellow. If you need neutral, you seperate them in such way that the PEN is directly connected to the PE bar and then linked to the N bar. At this point you make the TN-C-S type of system.
After the point that PEN is seperated into PE and N, they should NEVER be combined again.
Minimim allowed cross section of the PEN conductor is 10mm2 for Cu.

TN-S: you get seperate PE and N, no joining allowed. You join your own PE with the distributions PE.

TT: you get only N from the distribution, PE is yours, no joining allowed

IT: only 3 phases from distribution, no neutral, your own PE
 

Offline geggi1

  • Frequent Contributor
  • **
  • Posts: 440
First of all regarding the cross section of the PEN conductor.
The cross section of is different in different countries depending on the regulations used.
Here in Norway the regulations basically is that the PEN must be able to handle the same current as the phase conductor.
The reason for this is that with a single phase earth fault on a TNC or TNC-S system the full current will run through the N and PEN conductor back to the source.
This will ensure the quickest disconnect time at the protective device.

Second regarding connecting connecting the star point on a 3PH motor to ground or neutral.
Connecting to ground will most likely give you a earth fault trip or alarm depending on how your system is set up.
Connecting to neutral is not needed because when looking at the currents on the phases the vector sum is zero. If the protective device for your motor is a smart electronic one it might also nor work properly.
 

Offline capt bullshot

  • Super Contributor
  • ***
  • Posts: 3033
  • Country: de
    • Mostly useless stuff, but nice to have: wunderkis.de
But once in a while I run into handwavy arguments in favor of connecting it to neutral. For example here, and I frankly have no idea what they are talking about.
https://www.allaboutcircuits.com/textbook/alternating-current/chpt-10/three-phase-y-delta-configurations/
Quote
In a Y-connected system, there may or may not (Figure below) be a neutral wire attached at the junction point in the middle, although it certainly helps alleviate potential problems should one element of a three-phase load fail open, as discussed earlier.

OK, these circuits look like the stuff you've got to see in "Energietechnik" at university. The left hand side star isn't a motor at all, but rather imagined as a generator or secondary of a transformer. And they're talking about having a neutral line or not in transmission systems of electric energy. The three phase motor is a load (a balanced one, as others pointed out too) that never gets connected to the neutral.
Safety devices hinder evolution
 

Online magicTopic starter

  • Super Contributor
  • ***
  • Posts: 7158
  • Country: pl
I guess you're right :palm:

Although I still don't get their remark about neutral connection "alleviating problems should one element of a 3-phase load fail".
Maybe a reference to something in the earlier articles, but I'm not sure if I want to bother reading them all.
 

Offline capt bullshot

  • Super Contributor
  • ***
  • Posts: 3033
  • Country: de
    • Mostly useless stuff, but nice to have: wunderkis.de
"Should one element fail"

I guess this is e.g. about a load composed of three independent resistors or whatever. If one fails without neutral, you'll see a series connection of two resistors between two left over phases. In case neutral is connected, two resistors from each left over phase to neutral would remain.
In case your load is resistive indeed, this would result in quite different power consumption of the remaining circuit. Pointless for loads that rely on the three phase system, like three-legged transformers or motors (or electrical machines in general).
Safety devices hinder evolution
 

Offline mag_therm

  • Frequent Contributor
  • **
  • Posts: 783
  • Country: us
Yes, that article could be in relation to  residential service distribution in country like USA ( note the archaic units) where each user only has access to a single phase.
In that case the neutral is rated so that 2/3 of users stay on in event of one line failing.
Trees or lightning.

Another application is shipboard where some services stay on with  partial damage like ground fault on one phase.

Industrial services with 3 Phase loads like motors and transformers would want  all 3 phases to trip immediately to avoid damage like overloaded motors or cables.
Ordinary  industrial overcurrent  protection devices trip all 3. And some have trip on imbalance.
 